smoffo wrote: |
Thanks for the comments, going to scrap the idea of using the respirator cartridges. Just tested on of the fans(have two identical) and it seems to be moving air nicely. Specs says 2400litres/min. They are deigned for extracting gasoline vapor, so they should not ignite any vapor from airbrushing. For the next three to four months I can ventilate outdoors. I have the possibilty to adjust the speed of the fans as they are connected to a variable voltage supply. The problem that is the biggest is how to measure the air speed at the front of the booth? There are those small windspeed meters but I'm not sure if they are any good at this low speeds. For the filtering I have to do some thinking. Michael |
|
Michael,
Here in the U.S., 2400 liters/min is the same as ~85cubic feet per minute (cfm), not nearly enough to power your booth.
Let's say you want to make a booth with a face size of 2 feet X 2 feet. If you calculate the face area (2ft X 2ft = 4 square feet) and multiply that by a 100 fpm face velocity (recommended minimum), you come up with 400 cfm, the minimum needed to power a spray booth that size. Once you figure in filtration, duct diameter and length, any baffles, etc., you're faced with a bit of velocity loss. Depending on the variables, bumping up the cfm rating by as much as 25% will put you in the ballpark for correct fan performance.
Here are the metric conversions:
4 square feet = 0.37 square meters or 3716 square centimeters.
100 fpm = 30.48 meters per minute or 3048 centimeters per minute.
So, minimum face velocity = ~11,327 liters/minute (5 times your fan's capacity).
Now, if you were to construct a downdraft booth, you could almost halve the velocity recommendations (50 fpm instead of 100 fpm face velocity = 200 cfm for the same 2 X 2 booth), and you could possibly consider the use of an activated charcoal filter for that setup since velocity is slower. There would be some design differences, such as a plenum to even out the airflow underneath, and a perforated surface to spray on, but you could use a smaller (less expensive) fan.
By the way, those small portable vaneometers (airflow meters) work pretty reliably for checking airflow.
Gip Winecoff